Du nämner inte något om hur länge den varit ute.
Sensorn är självkalibrerande mot 400ppm
http://www.senseair.se/Datablad/k30%20.pdf :
Calibration
The default sensor OEM unit is maintenance free in normal environments thanks to the builtin
self-correcting ABC algorithm (Automatic Baseline Correction). This algorithm constantly
keeps track of the sensor’s lowest reading over a 7,5 days interval and slowly corrects for any
long-term drift detected as compared to the expected fresh air value of 400 ppm CO2.
Rough handling and transportation might, however, result in a reduction of sensor reading
accuracy. With time, the ABC function will tune the readings back to the correct numbers.
The default “tuning speed” is however limited to about 30 ppm/week. For post calibration
convenience, in the event that one cannot wait for the ABC algorithm to cure any calibration
offset, two switch inputs Din1 and Din2 are defined for the operator to select one out of two
prepared calibration codes. If Din1 is shorted to ground, for a minimum time of 8 seconds, the
internal calibration code bCAL (background calibration) is executed, in which case it is
assumed that the sensor is operating in a fresh air environment (400 ppm CO2). If Din2 is
shorted instead, for a minimum time of 8 seconds, the alternative operation code CAL (zero
calibration) is executed in which case the sensor must be purged by some gas mixture free
from CO2 (i.e. Nitrogen or Soda Lime CO2 scrubbed air). If unsuccessful, please wait at least
10 seconds before repeating the procedure again. Make sure that the sensor
Så om du inte vill/kan vänta på att självkalibreringen skall arbeta kan du jorda Din1 i åtta sekunder när sensorn är utomhus. Se databladet för mer information.